Errrrrr, we kind of like getting side-tracked here and probably one of mods is going to start locking the thread again...
Anyway, the Register have posted this statement from Telehouse..
<Quote>
Telehouse sent us the following statement:
We have a power distribution problem within the Telehouse TFM 6 room from approximateley 08:18 this morning.
One of the 2 power distribution units (PDU 2) in this room has suffered from a power failure to one of the 3 phase outputs caused by a burnt-out cable connection. Customer power connections from L1 phase are at present unavailable from this specific PDU.
We have prepared a power work-around. Unfortunately in order to bring this work-around into service we will have to isolate PDU 2 completely for a few minutes.
This action will cause the remaining 2 phases, L2 and L3, to be affected by a short duration power outage.
We plan to carry out this emergency action at 12:00 today.
This action does not affect any power supplies connected to the PDU 1 fitted in this room where duplicated power supplies are derived for certain customer power services.
</Quote>
Source URL:
http://www.theregister.co.uk/2006/08/17/telehouse_power_problems/
=========================